1000 amp gfi protection
wmthompson90
ky
electrician
How does one know if gear has gfi protection? Working with gear from Germany and waiting on unit specs.
It won't be there unless someone specifically specified.
I am willing to bet they did not. I have a temp on main inspection tomorrow and even if the inspector does not catch it, i will have to bring it up to him. We did not provide the gear yet rushed for power.
Don't you have drawings of the gear if it is being temped tomorrow?
what the code requires for 1000 amp or greater.
210.13, 215.10 or 230.95 depending on the circuit being a branch circuit, feeder, or service. Note that this only applies to solidly grounded wye systems having more than 150 volts to ground but not exceeding 1000 volts phase-to-phase.
This is a 480/277 wye system/systems
That may only be part of your problem. You need to assure the gear had acceptable NRTL certification.
I started in the trade in 08. I’m still green I guess. I’ll google it after this reply. I don’t know what that is or recall it in a code reference.
Yeah, electrical "gear" coming from overseas should ALWAYS be a red flag for compliance issues. Buyers for projects often are unaware that using foreign sources of electrical equipment is fraught with potentially EXPENSIVE problems getting it connected and passing inspection here. The suppliers overseas often don't know, don't understand or, in the case of China, don't even care that when it arrives, you can't connect it legally!
So aside from NRTL listing and the GF protection issue, what about SCCR? Yopur SCCR of the gear has to be equal to or greater than the available fault current. A lot of time even if they slap a UL label on something, they end up with a "courtesy" SCCR listing of only 5kA, which if it needs a 1,000A main, will be totally useless! Did anyone think to ask or are they just expecting you to "solve" that after the fact when it arrives? Because the rude awakening there is, you can't!