A Alwayslearningelec Senior Member Location NJ Occupation Estimator Dec 19, 2024 #1 What would you use to support the wire to the structure above? Guess that would depend if it was beams/steel decking or slab??
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Dec 19, 2024 #2 Sounds like a boiler plate specification. Are the ceiling grids being hung with ceiling wire?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Dec 19, 2024 #3 That's pretty much what our Building Inspectors require as much of our area is a siesmic zone. Our electrical inspectors advise the electricians of the requirement as that is who normally addresses it
A Alwayslearningelec Senior Member Location NJ Occupation Estimator Dec 19, 2024 #4 infinity said: Sounds like a boiler plate specification. Are the ceiling grids being hung with ceiling wire? Click to expand... Yes
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Dec 19, 2024 #5 Alwayslearningelec said: Yes Click to expand... So then you'll need 4 wires of equal or greater size than those holding up the grid.
L lordofthisworld Senior Member Location Massachusetts Dec 19, 2024 #6 U can use Caddy AB L-Brackets, they also sell AB L-brackets with pins for the hilt/ramset for concrete.