npavicic
 - Westland, Michigan
 - Electrical Inspector
A detached garage is wired with two separate 20-amp circuits. Receptacles and lights. Two conductors black & white with equipment ground. The contractor brought out a multiwire circuit. Three conductors black, red & white with equipment ground. The contractor then splices the white conductors from the two separate 20-amp circuits white ground wires in the j-box that come from the home service panel. There is a two-pole switch for the disconnect. Where there is an in and out with the conductors from a receptacle box, he does not pigtail the white grounded conductors. He explains this is not necessary since the connection is made in the J-box
from the home where the multiwire neutral is located. Is this a violation? Additionally, since both garage circuits are separate and only black phase conductors, should
the red phase conductor used on the other circuit be identified as the red phase? I would have expected the garage wiring to use three conductor w/ground throughout the garage. I appreciate any thoughts on this installation.