emu44
 - Jacksonville, FL
 - Mechanical Engineer
I have a fan replacement (Commercial HVAC) project where a customer requires motor redundancy, so they are going with ECMs. We are limited on amp draw due to their existing electrical architecture. The selection of EC Fans that we want to use gives the good reliability (redundancy) but at the cost of a higher overall FLA due to the extra motors, slightly too high for their electrical architecture. For the chosen EC Motors, they just require a 0-10V speed signal for modulation, no upstream VFD required.
This specific operating point they will be at does not require the motors to ever modulate more then 75%, even on a failed motor scenario, so the nameplate values will never be hit. This means that the actual amp draw would never be more than what their building can handle. We have the ability to limit the speed signal upstream to all motors via firmware so that we never send more then 7.5V.
The EC fan manufacturers already have a firmware limit inside of their motor controls in the motor itself that limits the performance and determines the OEM nameplate values. If that firmware limit is now upstream of the motor, does that mean we can/cant put a new nameplate on the motor?
In order to provide the required redundancy without having to rip out the existing architecture, could we put on a new nameplate on the motors that have the speed control limit applied? The motor manufacturer would have the ability to reflash the onboard firmware with new speed limits, but we have the capability to limit the speed on our own.
I cant find anywhere in the NEC that discusses software/firmware limitations on motors, maybe someone can point me in the right direction.