electroman00
 - Orlando FL
Is installation of Romex in Conduit or Raceway...code complaint...
Y/N
			Y/N
I'm not yelling, however why are you yelling?WHY ARE YOU YELLING? AND YES, MANY COMPLAIN ABOUT THE CODE.
Code reference?Only in dry locations, yes.
Which part?Code reference?
"Only in dry locations, yes."Which part?
334.12(B)(4)"Only in dry locations, yes."
That part!
300.9"Only in dry locations, yes."
That part!
BTW that answer "yes" is incorrect...
False.BTW if you were answering "yes" to my original question...you are incorrect...
If you use the correct name for "Romex" it's NM cable which is in the section I posted in post #8. As previously stated YES NM cable is permitted in raceways.In those code references does it say Romex?
Why ask a question that you’re so sure you already know the answer to?In those code references does it say Romex?
This means that materials used in electrical installations must not only be listed (tested and approved by a recognized testing organization) but must also be installed according to the manufacturer’s instructions and the conditions of the listing."Installation and Use." Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
To correct a wrong...is that a good reason?Why ask a question that you’re so sure you already know the answer to?
No, the correct answer yes. NM, NMC, NM whatever are cable assemblies.Again the correct answer is No...
Sorry forgot to hit Reply for your post...when I answered above.If you use the correct name for "Romex" it's NM cable which is in the section I posted in post #8. As previously stated YES NM cable is permitted in raceways.
Romex is a articular type of NMC that code does not directly and purposefully address for use in Conduits or raceways...or does it?No, the correct answer yes. NM, NMC, NM whatever are cable assemblies.
No. NM cables are permitted in raceways. If someone is saying that they are not they would be incorrect.Do you agree so far?