hbiss
EC, New York NEC: 2017
- Little Falls, New York NEC: 2017
- EC
I have been hit with this several times when dividing up tenant spaces, it can be quite a expensive item for an estimator to overlook.
Well, if you didn't realize that the tenant panels have to be accessible to the tenant, that's on you. If they are and not made accessible that's on the owner.
Another pitfall would be a large resort property with individual dwellings scattered about, think ranch type resort or YMCA retreat center with about 100 dwellings that are rented there is one large 7200V service to the property, everything else is feeders.
240.24(B)(1) requires each house to have access to the service of the property, which would be a 7200V service.
I would think that each dwelling would have a panel with a main breaker within it. However, to require that they also have access to 7200V switchgear is preposterous. That's like saying that a homeowner should have access to the utility companies' substation.
Sometimes you have to think a little bit.
-Hal