690.9(A)(1) Circuits Where Overcurrent Protection Not Required.
Overcurrent protective devices shall not be required where both of the following conditions are met:
(1) The conductors have sufficient ampacity for the maximum circuit current.
(2) The currents from all sources do not exceed the maximum overcurrent protective device rating specified for the PV module or electronic power converter.
690.8(B)(1) Without Adjustment and Correction Factors.
The minimum conductor size with an ampacity not less than the maximum currents calculated in 690.8(A) multiplied by 125 percent.
Exception No. 1: Circuits containing an assembly, together with its overcurrent device(s), if any, that is listed for continuous operation at 100 percent of its rating shall be permitted to be used at 100 percent of its rating.