480V, 3PH, 2HP motor feeder
pete25
I have a motor that is rated for 2HP, 480V, 3PH. The feeder originates from a 20A circuit breaker at a panel and terminates to a 30A fused disconnect with 15A fuses. Is the upstream 20A breaker in violation of NEC 430.62 as it is sized greater than the maximum allowed 250% inverse time breaker in table 430.52?
The 15 Amp fuses are the branch circuit protection for the motor. The feeder protection does not matter in this case.
IMO, if the feeder coming from the CB to the disconnect meets the tap rules it can be #14. Otherwise it would need to be #12. However, you might check the rules for sizing motor feeders to make sure I remembered this correctly.
Both the fuse and breaker are oversized for the motor SCGF Protection.
If the correct fuses were installed in the disconnect (6 amp), the breaker might be allowed dependent on the conductor size.
There are no motor taps here, its a single feeder serving a fused disconnect that terminates into a VFD.
It's not. There is no real question about wire sizing if it is a #12.
The question is that based on NEC 430.62(A) if you have a fused disconnect 15A fuses providing branch circuit OCP, your feeder OCP cannot be greater than the branch circuit OCP. My question is if I have a 20A CB at the panel terminating #12 awg to a fused(15A fuses) disconnect at the VFD, am I violating 430.62?
Your install is allowed by 430,62(B)
You have 20 amp conductors so the 20 amp breaker is fine.
(IMO, the fuse should be 6 amp)
See 430.62(B)
The size of the motor is basically immaterial.
The 20A breaker is a feeder protecting #12 which meets code.
The 15A fuses feed a VFD per the additional info provided in post #6.
The VFD needs to be programmed for the 2HP motor.
What size fuses are required by the VFD manufacturer? What is the full load rating of the VFD input?
My error, I( missed the VFD in Post #6.)
Confused . . to paraphrase (2020 NEC) 430.130(A) on SCGF protection when there is a VFD, it says for sizing the SCGF protection:
(1) use the normal procedure based on the motor FLC, but per Exception 1, if the VFD is listed and marked "Suitable for Output Motor Conductor Protection", you may use the normal procedure based on the VFD input current
(2) but if the VFD documentation has a lower limit, that lower limit applies
So it sounds like the the normal procedure based on motor FLC may be the controlling procedure. Are you saying that in practice in most every VFD circuit either (1) Exception 1 or (2) will in fact apply?
Cheers, Wayne