That doesn't follow. The outlet is a point, yes? "Where one or more receptacles are installed" doesn't specify whether that point is on the line side of the receptacle or the load side of the receptacle. For the reason jaggedben just pointed out, it makes more sense for the outlet to be on the load side of the receptacle.So the receptacle outlet is the point where the receptacle is connected to the premises wiring.
And that follows from the other definitions. "Premises Wiring System" includes "devices". A receptacle is a "contact device" per its definition. So the receptacle is part of the Premises Wiring System. The "point" on the wiring system at which "current is taken" is the face of the receptacle, not its line side terminals.
Cheers, Wayne