Receptacle outlets locations in doctor exam room office requirements.

Cartoon1

Senior Member
Location
Florida
Occupation
Electrical Engineer
Hi all,

I have a small commercial building for a doctor office that will basically consist of doctor office exam rooms. General doctor, nothing special. These rooms range from 70sq/ft to 120sq/ft each. I typically put receptacles about every 12' from each other, so each receptacle covers about 6' from each side. The doctor only wants 2 receptacles in the each room. I looked through the NEC and i saw that there is no general rule of how many receptacles is required in this space. I want to make sure that I'm not missing something. Since putting 2 receptacles only now will make the distance much farther for each receptacle from the other (more than 12 feet).

Thank you,
 
Hi all,

I have a small commercial building for a doctor office that will basically consist of doctor office exam rooms. General doctor, nothing special. These rooms range from 70sq/ft to 120sq/ft each. I typically put receptacles about every 12' from each other, so each receptacle covers about 6' from each side. The doctor only wants 2 receptacles in the each room. I looked through the NEC and i saw that there is no general rule of how many receptacles is required in this space. I want to make sure that I'm not missing something. Since putting 2 receptacles only now will make the distance much farther for each receptacle from the other (more than 12 feet).

Thank you,I
Install receptacle outlets according to the locations listed on the drawings . No wall space requirements
 