Alwayslearningelec
- NJ
- Estimator
What differentiates or determines the difference life Safety circuit from emergency circuits ? Thanks.
Well u can't run life safety circuits in the same raceway as normal power but u can run emergency (stand-by and optional) circuits with normal circuits. Also, u cant have life safety circuits in the same enclosures as normal power but u can have normal power circuits in the same enclosures with standby and optional emergency circuits. If u look at A700 which deals with life safety circuits, A701 which deals with standby systems, and A702 which deals with optional emergency circuits, these articles will let u know the differences between the circuits.What differentiates or determines the difference life Safety circuit from emergency circuits ? Thanks.
The word emergency should never be used to refer to Article 702 Optional Standby System as that creates confusion with Article 700 Emergency Systems. Article 701 is Legally Required Standby Systems.Well u can't run life safety circuits in the same raceway as normal power but u can run emergency (stand-by and optional) circuits with normal circuits. Also, u cant have life safety circuits in the same enclosures as normal power but u can have normal power circuits in the same enclosures with standby and optional emergency circuits. If u look at A700 which deals with life safety circuits, A701 which deals with standby systems, and A702 which deals with optional emergency circuits, these articles will let u know the differences between the circuits.
Actually "Life Safety" is a 517 system, it is pretty much aligned with 700 but the term "Life Safety Branch" stands alone.. If u look at A700 which deals with life safety circuits,
If you are trying to differentiate between loads that are Article 700 Emergency or Article 701 Legally Required Standby, look to your adopted building code. For example, if your adopted building code happened to be the IBC 2024, you look in Chapter 27 and anywhere it says Emergency Power System, you look at Article 700 of the NEC. If the IBC Chapter 27 says Standby Power System, you look at Article 701 of the NEC.What differentiates or determines the difference life Safety circuit from emergency circuits ? Thanks.
Actually 517.33, 517.34, and 517.35 spell the differences out quite thoroughly. ER's, ICU's, OR's, NICU's etc... would not have anything connected to the Life Safety Branch with the exception of FA, Exit signs, and egress lighting. For the critical Tasks 517.34(A) covers it as well as staff communications.Spent my last ten working years as an electrician in a large hospital. I asked several times about the emergency power / life safety breakdowns but never received any. The hospital purchased special cell phones that would only work within two blocks of the hospital for hundreds of nurses that worked there. Was confusing on every no ER,ICU, OR'S or NICU units where to pull 120 volt power from for charging stations.
Those systems legally required and classed as emergency by municipal, state, federal, or other codes, or by any governmental agency having jurisdiction. These systems are intended to automatically supply illumination, power, or both, to designated areas and equipment in the event of failure of the normal supply or in the event of accident to elements of a system intended to supply, distribute, and control power and illumination essential for safety to human life.
A system of feeders and branch circuits suppling power for lighting, receptacles, and equipment essential for life safety that is automatically connected to alternate power sources by one or more transfer switches during interruption of the normal power source.
...it goes on, but I highlighted the important part.A system comprised of alternate power sources and all connected distribution systems and ancillary equipment, designed to ensure continuity of electrical power to designated areas and functions of a health care facility during disruption of normal power sources, and also ...
Thanks. Even in retirement enjoy keeping up with NEC. Will be reading over these there 517 Articles. Besides Mike Holts great daily graphic read his & Charlie Trout daily code questions & enjoy EC & M magazine. The hospital that I retired from always went above & beyond minimums. One being that believe JACHO required that halve of hospital elevators be backed up by emergency power. They had over 20 elevators all backed up by emergency power. Elevator lobbies that had four elevators were on two different ATS'S so if one ATS failed two would remain operating. Same with ER AHCU'S.Actually 517.33, 517.34, and 517.35 spell the differences out quite thoroughly. ER's, ICU's, OR's, NICU's etc... would not have anything connected to the Life Safety Branch with the exception of FA, Exit signs, and egress lighting. For the critical Tasks 517.34(A) covers it as well as staff communications.
No. But if I was? ThanksAre you asking about Hospitals?
So when it comes to "critical" systems or "back up" power it can fall into??The word emergency should never be used to refer to Article 702 Optional Standby System as that creates confusion with Article 700 Emergency Systems. Article 701 is Legally Required Standby Systems.
The application of Articles 700 and 701 is triggered by rules in the building and life safety codes.
Correct.701 and 702 wouldn't be considered emergency???
If you weren't asking about healthcare, then where did you come up with the term "Life Safety"? As Roger stated in post 5, the term is exclusively a healthcare term in regards to the NEC.No. But if I was? Thanks
2023 NEC moved all definitions to art 100. Before then if a definition was only used in one section (like 517) it appeared in the XXX.2 portion of that section and the definition only applied to use in that section. Art 100 was for definitions that applied throughout all of NECNotably, "Life Safety Branch" is only used in article 517 as far as I know, where it is described as part of the 'Essential Electrical System', which is also defined in article 100.
As I think Roger was implying, if the plans say life safety in reference to circuiting, wiring or panels, on a project other than healthcare they are using it improperly. Life Safety is one of the essential systems in healthcare, only.So when a drawing note says "life safety" what article is that? All three?
And I think NEC should have left definitions that only apply to one section of the document within the section it applied to. This would have been one of them.As I think Roger was implying, if the plans say life safety in reference to circuiting, wiring or panels, on a project other than healthcare they are using it improperly. Life Safety is one of the essential systems in healthcare, only.