Lighting outlet

Danielinho

Member
Location
Texas
Occupation
Electrician
Does 210.70 (C) apply to air handler located above bathroom shower or laundry room with no attic space or walkable space? I’d think so since it mentions “contain equipment requiring servicing” I’d just like to make sure. Thanks in advance
 
Just for clarification, how do you access the air handler?
 
Oh yes, there will be an access panel, the space I’d say is about 3 ft tall, enough space for an air handler for a townhome
Will there be sufficient illumination with the access panel open?
 
So you would stand on a ladder in order to work on the AH?
 
I would install a box for the lighting outlet instead of spending much time worrying about it. Then blank off the box. 210.70 only requires the lighting outlet, it does not require a fixture.
 