I’m just wondering what everyone thinks about wiring residential receptacles all on one 20A 120V circuit, no matter the size of the house or location. I have someone who’s wanting this done no matter what. Front of house, back of house, each side of house, all levels of house. Is this a good practice tho his reasoning is that they don’t have to worry about finding if it’s a GFCI or regular duplex. I don’t particularly like this practice of having 15, 20, or even more outside receptacles on one circuit with 1 GFCI device. They’re saying that they don’t want to have to, upon trim-out, have to use a meter out whatever to locate where the GFCI is to be place. It seems that, even if the conductors are mark, that it’s easier to just slap in regular receptacles of WR type and be done with it. I say it’s laziness to not figure out 100% of where the GFCI devices goes.
Let me know what you think and if you agree with him.
Something I’ve found online: A GFCI, whether as part of a breaker or combined with a pair of receptacles, is only monitoring for a difference between hot & neutral - i.e., watching for some current to go missing. As long as the total is less than the capacity of the GFCI device, which itself should be matched to the capacity of the overcurrent protective device (fuse or circuit breaker), it really doesn't matter how many receptacles or devices are connected.
There is a theoretical issue as follows:
A typical GFCI trips in the range of 4-6ma. You could have a bunch of devices that each leak 1-2 ma, which is generally safe. The cumulative effect of these devices on one circuit (which could easily be with as few as 4 receptacles, so you don't need "lots of receptacles" for this to happen, but the more you have, the more likely it will happen) would be enough to trip the GFCI. Yet when you go back to the "unplug everything and plug in one at a time to see where the problem is", the problem device might never be identified - and yet the tripping would continue.
More that I’ve found online:
When using a GFCI device, consider the following guidelines for downstream receptacles.
Let me know what you think and if you agree with him.
Something I’ve found online: A GFCI, whether as part of a breaker or combined with a pair of receptacles, is only monitoring for a difference between hot & neutral - i.e., watching for some current to go missing. As long as the total is less than the capacity of the GFCI device, which itself should be matched to the capacity of the overcurrent protective device (fuse or circuit breaker), it really doesn't matter how many receptacles or devices are connected.
There is a theoretical issue as follows:
A typical GFCI trips in the range of 4-6ma. You could have a bunch of devices that each leak 1-2 ma, which is generally safe. The cumulative effect of these devices on one circuit (which could easily be with as few as 4 receptacles, so you don't need "lots of receptacles" for this to happen, but the more you have, the more likely it will happen) would be enough to trip the GFCI. Yet when you go back to the "unplug everything and plug in one at a time to see where the problem is", the problem device might never be identified - and yet the tripping would continue.
More that I’ve found online:
When using a GFCI device, consider the following guidelines for downstream receptacles.
- You can daisy chain up to 12 outlets off a single GFCI outlet, but it is recommended to limit the number to no more than 8.
- The total load connected should not exceed the rated amperage and wattage of the GFCI.
- Installing the GFCI receptacle on the first outlet allows GFCI protection for every wall outlet downstream, but only if the downstream outlets are connected to the load terminal of the GFCI.