hhsting
- Glen bunie, md, us
- Junior plan reviewer
I have disconnect inside walk in freezer. Quick question what is the typical nema rating for disconnect inside walk-in freezer?
Or 4X
Why such extremes?OR type 6 or similar water-tight enclosures.
Until the door is left open, like during loading/unloading, then the humidity builds up pretty fast.Leave something unwrapped in a freezer and it will become dehydrated.
Why such extremes?
4X is for corrosive environments. Type 6 is for submersion at limited depth.
Any of the Type 3 version are rated for damp and operation with ice covered.
My preference would probably be a combination 3R/12 style.
Never a need for Type 6 unless it is being submerged.just options. they all work.
I don't know what they plan to do in the freezer. I have seen places do some food processing in freezers or hose them down occasionally. They needed disconnects for the processing equipment. NEMA 4 or 6.
If it is just dry freezer foods being stored like in a grocery store then it likely won't matter.
But does that humidity cause rain on your equipment inside? If it does, I could see requiring 3R, otherwise seems like Type 1 would suffice.Until the door is left open, like during loading/unloading, then the humidity builds up pretty fast.
Non-metallic makes sense for these type of environment. Personally, I don't like any electrical in most small walk-in freezersI have seen some Nema 1 enclosures fully rusted or pitted out in walk-ins / cold rooms. But it was industrial and there was discussion that the area was being hosed down or brought to room temp daily creating condensation on the terminals and wires.
On the other hand, if that humidity can penetrate the equipment before condensing inside, maybe an enclosure type that would prevent the entrance of ambient air is appropriate?
Cheers, Wayne
Would not nema 4X be good for walkin freezer in restaurant or nema 3R? Which?
Use NEMA 3 which is overkill but will have you covered. If you get a chance, go into a walk in freezer and look at the evaporator(s), their wiring is open and NEMA 1 at best.No one
The OP's job is as a plan reviewer. So the question is whether a NEMA 1 disconnect (or lack of specification on the plans requiring something other than NEMA 1) should be rejected at plan review or not.Use NEMA 3 which is overkill but will have you covered. If you get a chance, go into a walk in freezer and look at the evaporator(s), their wiring is open and NEMA 1 at best.