Explain ??

Therealcrt

Senior Member
Location
Kansas City
Occupation
Electrician
I have a video I took, can I not post it here? It involves Me testing power at a socket of a 8 foot fluorescent fixture. I took one lead to the socket the other lead to a conduit a.k.a. ground and I read 515 V.
 
I have a video I took, can I not post it here? It involves Me testing power at a socket of a 8 foot fluorescent fixture. I took one lead to the socket the other lead to a conduit a.k.a. ground and I read 515 V.
The ballast is a type of transformer. It raises the voltage to fire the fluorescent tube.
The voltage was probably way higher than that. You can't really measure voltage from the ballast with a regular meter and get any sort of true reading.

As for the video, you would have to upload it to Youtube or other video storage platform, then post the link here. I've never tried to post a video other than through Youtube.
 
The ballast is a type of transformer. It raises the voltage to fire the fluorescent tube.
The voltage was probably way higher than that. You can't really measure voltage from the ballast with a regular meter and get any sort of true reading.

As for the video, you would have to upload it to Youtube or other video storage platform, then post the link here. I've never tried to post a video other than through Youtube.
515 volts is 515 volts whichever way you look at it. So what meter do you use?
 
Based on working on a lot of fluorescents, try a known good lamp first. Sometimes the lamp pins don’t engage the contacts in the tombstone
Next is replace the ballast
If the lamps are T12, and old ballast, replace with T8 and electronic ballast
Or a new LED luminaire
 
Based on working on a lot of fluorescents, try a known good lamp first. Sometimes the lamp pins don’t engage the contacts in the tombstone
Next is replace the ballast
If the lamps are T12, and old ballast, replace with T8 and electronic ballast
Or a new LED luminaire
Can you replace a ballasted tube with an LED without removing the ballast?
 
Can you replace a ballasted tube with an LED without removing the ballast?
If you are asking what I think you are asking, there is some hybrid lamps out there that will run off a ballast or directly connected to the line voltage and is very common to find LED lamps that only work when connected to the ballast .
 
515 volts is 515 volts whichever way you look at it. So what meter do you use?
True RMS meters can give you different readings particularly when dealing with distorted wave forms which can be expected with an electronic ballast. These ballasts don't necessarily have same voltage when a lamp is installed or at least after it has lit up. A high pulse can be needed with the fluorescent tubes to start the arc in the tube.
 