Say I have 4 current carrying conductors in a raceway. They have been derated in accordance with 310.15(C)(1) to 80 percent of their ampacity. The conductors then enter an enclosure and go through a nipple that is less than 24in long into switchgear. I know derating does not apply inside boxes or nipples shorter than 24in. With that said, is it compliant to reduce the conductor size upon entering the enclosure?
In this scenario, I essentially have 5 parallel runs of 600 Kcmil conductors, 3 hots and neutral per raceway. Neutral is being counted as current carrying per engineering. OCPD is set at 1800 amps.
My derating is as follows:
600 Kcmil CU @ 90 degrees- 475A
475A x .80 = 380A x 5 runs = 1900A
I want to reduce my conductor size upon entering my enclosure to 500Kcmil CU class K stranded THHN due to extremely limited space in the switchgear. (Existing installation, just trying to make it work)
500 Kcmil CU @ 75 degrees- 380 A
380A x 5 sets = 1900 A
Does anyone see issues with this, and if you do, please point me towards a code reference. Thank you.