ElecBeginner
- Hawaii
- Engineer
Hello All, I've been looking into my local voltage drop calculator and various online calculators online and spent the better half of the day trying to understand whats going on.
I am under the assumption
VD(single phase) = I x Z x L/1000 x 2
I = VA/V = Watts/(V*PF)
PF = Cos(theta) = Watts/VA
Z = Rcos(theta) + Xcos(theta)
With the above ive been trying to recreate the results i see in various VD calculators and getting a result that is off by a factor of PF.
Example:
120V, 1ph, 12000 watts, 0.9PF, 10ft, #12 copper wire in PVC (numbers arbitrarily chosen, the result ends up the same for different values)
using the equation above i get
VD = 12000watts / (120V x 0.9) x (2 x cos(25.8) + 0.054 x sin(25.8) ) x 10ft/1000 x 2
= 4.07V
Using the Calculator i get 3.65V (which is 4.07 x 0.9), this includes other calculators i find including southwire, the one recommended by mike holt, and other miscellaneous calculators.
Not sure how to add an image but ive used excel to compare and its generally always off by a factor of PF, so the question is am I missing a variable somewhere or converting real vs apparent parent wrong somewhere or something else altogether? Any help would be appreciated.
Example:
= 4.07V