Your sensing connection is on either the load or the generator side of the switch. Could you maybe have the grid and generator connections reversed?Yes motorized with PLC control and yes but for reason it goes back to normal and generator shuts down.
Thompson ATS
You have to tell the PLC that you want to load test. If you just open the breaker when the controller thinks it should be closed, it will try to reclose.Yes motorized with PLC control and yes but for reason it goes back to normal and generator shuts down.