The electron man
- Nyc
- Electrician
I get that but if the neutral is not being used how dose the current make it back to the source
Only the long wire labeled N in your drawing, from the neutral bar on the left to the 3-way N junction, has 0 current. The other two shorter N wires to each load each carry current.Question regarding mwbc if i have 2 equal loads the neutral will have zero current flow and the circuit will operate as a 240v circuit, my question is if the neutral is not being used and you have 2 separate loads how is the loop created to complete circuit
So were dose the current go once it reaches the j boxOnly the long wire labeled N in your drawing, from the neutral bar on the left to the 3-way N junction, has 0 current. The other two shorter N wires to each load each carry current.
So the loop is black - load 1 - short N1 wire - short N2 wire - load 2 - red.
Cheers, Wayne
It comes in N1 and out N2 (or vice versa), where N1 and N2 are the short N wires on the right.So were dose the current go once it reaches the j box
You just gave me the aha moment now i see how the loop is completed through the short neutrals you the manIt comes in N1 and out N2 (or vice versa), where N1 and N2 are the short N wires on the right.
In other words, if you are thinking that at the same point in time that current is flowing towards the junction box in both N1 and N2, that is not correct for this configuration.
If you look at post #3, current is flowing towards the loads in the black conductor, and away from the loads in the red conductor. In the opposite half of the cycle (1/120 seconds later), current will be flowing away from the loads in the black conductor, and towards the loads in the red conductor.
Cheers, Wayne
I think what tripped up the OP is this:Basically if you have 2 valid circuits, you can add them up and still have a valid circuit.
At any instance in time, the two hots are at opposite polarities. When one is positive, the other is negative.I get that but if the neutral is not being used how dose the current make it back to the source