JovialBulge
- New England
- Automation Dude
If I have a VFD that is rated HP=25.0, Output Amps=37.0, Max Input Amps=33.7, 480VAC and I am getting just a bit fuzzy on the Class J fuse sizing for the line side of the drive. The 25HP motor that the drive is controlling has a nameplate FLA of 29.50A @ 480VAC, using table 50.1 in the UL document that motor has an FLA of 34A. It's my understanding that I need to use the values within table 50.1 when doing any FLA calculations for the main incoming disconnect for the panel overall, however does that rule apply here as well?
In this case the manufacturers table shows a Min and Max fuse rating for non-UL applications, 45A and 70A respectively. Then they give a MAX rating for a fuse in a UL application of 70A. With my max input amps to the drive being 33.7, should I be using 33.7 x 1.25 = 42.125A and then rounding down to 42A and choosing the next common size of 45A on the fuse? Should I be using 33.7 x 1.50 = 50.55A and rounding up to 51A and then choosing the next common size of 60A on the fuse?
I know that the minimum ampacity of the wires feeding VFD is 125% of the rated input current of the drive as per 430.122(A).
First I read...5.2 in the UL508A doc "For calculations involving amperes, calculations resulting in a fraction of less than 0.5 shall be rounded down to the next whole number. Calculations resulting in a fraction of 0.5 or more shall be rounded up to the next whole number."
Then I read...31.3.2 The branch circuit protection for a single-motor circuit provided with a variable-speed drive shall be of the type and size specified by the manufacturer's instructions provided with the drive. Lower sizes, of the same type, can be used. When the instructions do not specify the type and size, a branch-circuit fuse or inverse-time circuit breaker shall be used and shall be sized in accordance with 31.3.1(a) based upon the full-load motor output current rating of the drive.