MWBC Romex capacity at 208/120 (3W 1ph) vs 120/240 home power
Flicker Index
Pac NW
Lights
While all three conductors are considered current carrying conductors, they don't add up the same way.
If you put a 120v 1200w light bulb on each pole, you'll have 10A on each line. In 120/240, the neutral will carry zero or negligible amount of current.
In 208/120 3W 1ph, all three conductors will carry 10A, thus 1.5 x the I^2R loss within the same jacket.
Does this have to be taken into consideration?
Yes, you have to count the neutral as a current carrying conductor for derating purposes when two of the three phase conductors are used. Not so for 120/240 V.
The way you’re describing your scenario, you will have 3 bulbs in the 3 phase case, so the load is 1.5 times. So losses are proportionally equivalent.
The title should say 120/208 rather than the 208/120, but the parenthetical comment clarifies that it is 3W 1ph. So there are only two bulbs, and the losses are proportionally more (3 CCCs @ 10A rather than 2) than on 120/240. Add a 3rd bulb on a 208Y/120, and your comment applies.
Cheers, Wayne
The title should say 120/208 rather than the 208/120, but the parenthetical comment clarifies that it is 3W 1ph. So there are only two bulbs, and the losses are proportionally more than on 120/240. Add a 3rd bulb on a 208Y/120, and your comment applies.
Cheers, Wayne
Missed that! Thanks.
It does, but the ampacity adjustment factors don't make any real difference with 15 and 20 amp circuits until you have more than 9 current carrying conductors in the cable. That is based on most modern wiring have conductors that are rated 90°C.
I don't know how many times I've heard, " you have 4 cables bundled, you need to derate.". Yeah I did, nothing changed 😇