Thanks very much. I' not getting the concept/parameters of dropping down to a smaller wire when needed larger for VD. In my case I need #8's for the recept but then obviously I can reduce to #12's. WHY AND WHEN CAN I REDUCE? You have to have #8's for a particular portion? EXACTLY HOW MUCH OF THE RUN DO YOU NEED THAT LARGER WIRE SIZE(#8's).
Increase of wire size reduces resistance on the conductor, resistance causes the voltage to drop,
If over a specified needed distance the amount of voltage drop would either be contra indicated by a code requirement or for operation of a device or equipment, you can upsize a conductor, reducing resistance and increasing voltage (more accurately maintaining voltage).
The only limiting criteria for reduction of the conductor after determining the need to upsize the conductor for VD is that the reduced wire size is adequate for the amperage of the overcurrent device supplying the conductors. The length of a reduced conductor post increase for VD is only limited by the need for the maintenance of a specified voltage to the end device.
EXACTLY HOW MUCH OF THE RUN DO YOU NEED THAT LARGER WIRE SIZE(#8's).
Without your voltage and amperage requirements can't answer specifically, as any change to either of these criteria will change the outcome.
That is a function of voltage demand and amperage requirements. Southwire has an app to plug in the various data to calculate the max length. What is the voltage requirement and amperage requirement, total length of the run?
With a manual calculation You can play with the numbers comparing various resistance and reactance of different conductors over a specified length and come up with a desire max length for the #8 and still maintain the minimum of voltage drop. Table 9 of the NEC has the the resistance and reactance of different conductors in different conditions, and the enhance content have some math examples for using specific criteria from the table.
The Amperage required for the calculation MAY NOT BE the breaker amperage but can be the operating amperage of the equipment, like in my example in previous post.
The reversing of this process is also useful to reduce AFC to a piece of equipment, Adding length or reduced size (last one limited by max amperage of the conductor) will add resistance and reduce voltage available. This is really a balancing act for maintaining a minimum voltage while reducing potential impact of available fault current, so not always the best way to meet the AFC to a piece of equipment's SCCR.