Ponchik Senior Member Location CA Occupation Electronologist Mar 5, 2025 #1 (2) 3" conduits installed for an angle pull. Allowing for the lock nuts, I calculate the size of the pull box to be a minimum of 13"x13". The 13x13 is not standard so I have to go to 16x16. Correct?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Mar 5, 2025 #2 Ponchik said: The 13x13 is not standard so I have to go to 16x16. Click to expand... Angle pull is 6X the raceway trade size plus the additonal raceway in the row. You also need a minimum of 18" (6X3) between the raceway entries.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Mar 5, 2025 #3 A picture is worth a 1000 words
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Mar 5, 2025 #5 Another example of the raceway spacing.
