I agree. The arguement against it was that it’s not a listed strap. My thoughts were since there is no strapping requirement for THHN in panel boards, this would not need to be listed since it’s not a code required strap. It would be a supplementary strap.No, what would it violate?
As you've stated there is no requirement to bundle the conductors together so nothing is required. Personally I would use a cable tie but to each his own.I agree. The arguement against it was that it’s not a listed strap. My thoughts were since there is no strapping requirement for THHN in panel boards, this would not need to be listed since it’s not a code required strap. It would be a supplementary strap.
Yes I agree. What about the copper and aluminum conductors touching?As you've stated there is no requirement to bundle the conductors together so nothing is required. Personally I would use a cable tie but to each his own.
Not a problem.Yes I agree. What about the copper and aluminum conductors touching?
Code wise or corrosion wise?Not a problem.
Either. Copper and aluminum touch all of the time in panels without any issue. You can even use bare copper condcutors in aluminum raceways.Code wise or corrosion wise?
Where do problems arise with two dissimilar metals touching and what does the code say if anything? Like diox on aluminum lugs.Either. Copper and aluminum touch all of the time in panels without any issue. You can even use bare copper condcutors in aluminum raceways.
Anti-oxidation paste is not required on terminals listed for aluminum conductors. It might be a good practice to use it since it's cheap but it is not required. The dissimilar metal issues can arise in corrosive environments. We connect dissimilar metals together all of time without any issues. The most common connection is copper and Galvanized steel.Where do problems arise with two dissimilar metals touching and what does the code say if anything? Like diox on aluminum lugs.
any issues in damp environments?Anti-oxidation paste is not required on terminals listed for aluminum conductors. It might be a good practice to use it since it's cheap but it is not required. The dissimilar metal issues can arise in corrosive environments. We connect dissimilar metals together all of time without any issues. The most common connection is copper and Galvanized steel.
Shouldn't be an issue. Aluminum conductors are used outside all of the time.any issues in damp environments?
It’s hard to know this stuff man. Google is just wrong about it. As well as chat gpt/grok.Shouldn't be an issue. Aluminum conductors are used outside all of the time.
Search engines are poor at getting the facts straight because they glean info from unreliable sources. The internet is full of misinformation.It’s hard to know this stuff man. Google is just wrong about it. As well as chat gpt/grok.
Remember there needs to be an electrolyte present for galvanic corrosion to occurWhere do problems arise with two dissimilar metals touching and what does the code say if anything? Like diox on aluminum lugs.
Can you explain that?Remember there needs to be an electrolyte present for galvanic corrosion to occur
Yes indeed. That’s why professionals exist.Search engines are poor at getting the facts straight because they glean info from unreliable sources. The internet is full of misinformation.
A conductive liquid. Usually it's water for our purposes. And remember pure water is actually not a very good conductor.Can you explain that?
What causes the lug corrosion in older panels?A conductive liquid. Usually it's water for our purposes. And remember pure water is actually not a very good conductor.