electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
Does the utility ground the wye point or leave it floating?I've run into a few of these, always kind of freaks me out. I think it happens when a utility replaces an old transformer with a delta on the customer side with one that has a WYE on the customer side on an 3W service. They don't run a neutral to the customer since there is no place to land it in the existing 3W service equipment. From the customer's point of view it's still a 3W ungrounded service, so they are happy they don't have to change anything. Since there is no neutral at the service entrance equipment I still treat it as an ungrounded service for the PV system interconnection.