Hi, My PV permit was rejected because AHJ states only one PV breaker is allowed per Service Panel and they mention that only one dedicated output breaker is permitted per 705.12 2017 NEC.
Article 705.12(B)(1) States that ONE or MORE power source shall have its own circuit breaker or fusible disconnect means. ( One per Power source )
Article 705.12(B)(2)(3)(b) or commonly known as 120% rule for back feed breaker at the opposite side of the bus bar specifically mention .......power source(s) ..... referring at the possibility to have more than ONE power source (on our project Two Back feed breaker at the opposite end of the bus bar)
Am I misunderstanding this ?