The bus bar is 200A and I am going to derate the main breaker from 200 A to 175A in order to comply with the 120% ruleI was just trying to piece together what the AHJ might be saying so that you can better prepare to debate them or make a revision to get a fast approval.
In this case, it would be easier to verify the panel's busbar rating of 225A and then just use (a). Then you could see if the AHJ approves it. I think they are just interpreting the 120% rule incorrectly or differently than usual. It might be more difficult to get them to see it your way than it would be to adapt and move on.
If the busbar is not 225A, then I would just put in a PV combiner breaker panel next to the service panel. It shouldn't add much of a cost.
30A ( New PV System) + 20A (Old PV System) + 175A < 200 x 1.2
225A < 240A