One supply house out of three does.As far as I can tell none of the Leviton distributors around me stock the load centers. Even when searching online its seems to be exclusively an HD and Amazon line. Do many suppliers around you stock them?
Reminds me of Trilliant load centers.
This could be an available fault current issue. In the Phoenix area the utilities provide an default AFC at the service, which is generally over 10KAIC for a 200 amp residential panel. The local jurisdictions require that we use the utility value at the service and do not allow AFC calculations for the service lateral or drop. Leviton will not series rate with Siemens, so the Leviton would either need 22KAIC branch circuit breakers for fully rated or a 22KAIC or higher main so that the panel would be series rated as a unit.I wonder why they used a main breaker panel as a sub panel.
That's not what a Lock Out Tag Out is. A LOTO would be a means to secure a breaker in the panel in the off position instead of a disconnect at the equipment location.It's a 2025 build, so there's an external disconnect. Would that be appropriate for a LOTO?
Doesn't everybody? LOL.I wonder why they used a main breaker panel as a sub panel.
Curious as to who here are using the Leviton load centers?
In my area a 200A 42 circuit w/ cover is around $170.00
Breakers are competitively priced with Homeline and Siemens.
Aren't there 3 breaker lockout devices in the photo?What is available for LOTO on these? No typical toggle to attach to.
Pop the breaker out. The conductors don't connect to the breaker.What is available for LOTO on these? No typical toggle to attach to.