"The 125 percent multiplier for a continuous load as specified in 210.20(A) is included, therefore no additional multiplier shall be required when using the unit loads in this table for calculating the minimum lighting load for a specified occupancy."
I don't understand this note. The 125% multiplier in 210.20(A) is for the conductor and OCPD of a branch circuit. I don't see how this has anything to do with calculated loads of a feeder or service which is what 220 Part 3 is about. Is it saying I don't need to add the extra 25% when I determine the quantity of the branch circuits I need for lighting?
	
		
			
		
		
	
				
			I don't understand this note. The 125% multiplier in 210.20(A) is for the conductor and OCPD of a branch circuit. I don't see how this has anything to do with calculated loads of a feeder or service which is what 220 Part 3 is about. Is it saying I don't need to add the extra 25% when I determine the quantity of the branch circuits I need for lighting?
 
				
 
 
		