designer82
- Boston
I would scrap the wireway. Feed the CT directly with 3 sets and the 600 directly with 2 sets.Found out the main needs to be 1,600A and commercial side 1,000A.
I am thinking to just do it like this below and not worry about the meter stack configuration.
What do you guys think?
I Agree. I would scrap the 1600A disconnect too.I would scrap the wireway. Feed the CT directly with 3 sets and the 600 directly with 2 sets.
I haven't been around much for multi tenant situations with that sort of need.Are you sure you can do a 1000A Ct cabinet? I know they exist but are rather rare as most utilities (in my experience, YMMV) require a switchboard or switchgear metering section above 800A.
Most larger capacity services I get involved with is usually one transformer for a dedicated customer and they put CT's right on the output spades of the transformer. They may mount the meter on the transformer or seems to be even more common to place the meter on a separate post next to the transformer - seen a little of both, not sure what the reasoning is for one way vs the other. That is mostly the rural POCO's that will do that. There is another POCO that wants a CT cabinet regardless in almost all cases. I suppose it does simplify things some in the case of needing to change out the transformer and can see that being a reason they want the CT cabinet nearly all the time.
They could but most won't. They have design standards that they seldom will vary from no matter the situation.I would think the Poco could just put the CTS around the desired conductors and skip the others?
That's an extra $19/month meter charge. Not sure about capital cost, 2 CT set ups could be less than a switchboard with metering section, if thats what they would require.To simplify things, I'm thinking I'll just change it to 2 (600A each) CT Cabinets/meters for the one commercial tenant. Let them have 2 meters, so what.
They make CT cabinets from 400 - 4000.I appreciate all the valuable feedback!
I was reading the National Grid Standards and they do in fact seem to have some wording on "transformer rated CT Cabinets 400-800 Amp".
So it may be that they cap at 800 Amp.
I reached out to them but they'll take a long time to answer and prob. won't even understand what's going on.
You need a better group of product reps to educate on what your material options are.
Most of the time when this happens on a service of this size, we are required to use a bused CT cabinet. I think you can get up to a 4000 amp rated bused CT cabinet.Yeah kind of an interesting situation for the op, if the utility usually just meters at the spades, because he would want the thousand amp set metered at the transformer but then an unmetered set to feed the meter Bank. I would think the Poco could just put the CTS around the desired conductors and skip the others?