Overcurrent protection
Alex_rg15
Texas
What size inverse time circuit breaker should be installed for a group installation to protect the following 208 V, three-phase motors? One 7.5-HP motor, two 10-HP motors, and one 15-HP.
Step 1
Find the FLC for each motor
From NEC Table 430.250:
• 7.5 HP motor: 24.2 A
• 10 HP motor: 30.8 A
• 15 HP motor: 46.2 A
Step 2
size
Calculate the maximum allowable circuit breaker
Apply NEC 430.52:
• Maximum breaker size
= (2.5 X FLC of largest motor) + sum of FLCs of otl
=(2.5×46.2 A) + 24.2 A + 30.8 A + 30.8 A
= 115.5 A + 24.2 A + 30.8 A + 30.8 A
• Maximum breaker size = 201.3 A
Step 3
Select the standard circuit breaker size
Solution
The size of the inverse time circuit breaker should be 225 A.
But in the answer they give me 200 A
May be I’m doing something wrong I just copy and paste the question to google, and google give a 200 A answer, But google give me 42 A for the 15 HP 208V 3-phase motor, I check the table 430.250 and shows 46.2
Thank you
Google used 230 volts for the 15 HP not 208 volts.
Step 3
Solution
Thank you
430.52 is for individual motors. You want 430.53.
The rating of the OCPD for the largest motor would be 46.2Ax2.5=115.5A ==> 125A OCPD (next size up)
Per 430.53(C)(4):
125A + 30.8A + 30.8A + 24.2A = 210.8.A. A 200A OCPD would be the correct size (225A exceeds 210.8A)
Step 2
size
Apply NEC 430.52:
Step 3
Solution
As mentioned the (115.5 A) should be a
Per 430.53(C)(4):
SCGFPD number in this case 125 amp breaker.
Then add motors.
Then round down accordingly via 240.6