Hello everyone, I have a job that's getting push back right now on the way I sized the refrigeration/condenser/HVAC loads that need to be backed up by the generator set. I sized all of the loads based on the nameplate on the motors. I used MCA × sqrt 3 x 480 for the 3 phase motor loads and used the MOCP for the breaker sizes. They're telling me I need to use a diversity factor for the loads but I have never used a diversity factor for emergency backed refrigeration/HVAC equipment. I can't find anything in the NEC about it (I did see where it talks about lighting and receptacles but not motor loads), can anyone help me