Island Receptacles in a drawer?

JoeNorm

Senior Member
Location
WA
Would a receptacle within a drawer of an Island be permitted according to the new code? Would like to avoid the receptacle in the countertop if at all possible.
 
Would a receptacle within a drawer of an Island be permitted according to the new code? Would like to avoid the receptacle in the countertop if at all possible.
As letgo stated they are not code complaint under the 2023 NEC. The wording is very specific in that the receptacle must be in the countertop.
 
The wording is specific that the receptacle must be in or above _a_ countertop.

If you have a split level countertop, then the receptacle can be in the riser between the two. See this image from NFPA itself (this image is _not_ code, but indicates that at least someone at the NFPA holds this interpretation):
1743080588525.png
So my question, relevant to the OP: just how large does the lower flat surface need to be to count and permit a receptacle in the riser between the two 'countertops'. IMHO you could have a place an outlet at the side of an island if it was shielded from below by a sufficient 'vestigial countertop' (possibly with some sort of raised rim) so that there are no dangling cords that a kid could grab or an adult could accidentally brush into; in other words, a 'vestigial countertop' that eliminates the risk presented by cords in the side of the island.
 
The wording is specific that the receptacle must be in or above _a_ countertop.

If you have a split level countertop, then the receptacle can be in the riser between the two. See this image from NFPA itself (this image is _not_ code, but indicates that at least someone at the NFPA holds this interpretation):
View attachment 2576378
So my question, relevant to the OP: just how large does the lower flat surface need to be to count and permit a receptacle in the riser between the two 'countertops'. IMHO you could have a place an outlet at the side of an island if it was shielded from below by a sufficient 'vestigial countertop' (possibly with some sort of raised rim) so that there are no dangling cords that a kid could grab or an adult could accidentally brush into; in other words, a 'vestigial countertop' that eliminates the risk presented by cords in the side of the island.
Or a pull out countertop?

What if you had a drawer front attached to a pull out countertop that has a receptacle hidden behind the drawer front?

Rob G - Seattle
 
Or a pull out countertop?

What if you had a drawer front attached to a pull out countertop that has a receptacle hidden behind the drawer front?

Rob G - Seattle

So a _fixed_ receptacle, on the side of the island, but protected from below by a pull out countertop with a barrier (the drawer front), so the pull out surface becomes a barrier that prevents access to the cord from below, and prevents the cord from falling off the pull out countertop?

I really like it.

I wonder if this could be small enough to be part of a fancy device box. Have a single device box with all the drawer hardware built in? It would also be nice for things such as phone charging shelves.
 