Light Sabre
- Colorado
- Electrical Inspector
Is there a chart that sizes bonding screws somewhere? If you have the right size bonding screw as the main bonding jumper, is this adequate for the GEC to terminate with the EGC bus? Do the manufacturers size these screws for this connection, and if so, from what chart are they being sized? I have some inspectors that say it’s ok to use the bonding screw that comes with the equipment to bond the GC to the EGC, and then terminate the GEC to the EGC bus.
My interpretation is that it has to make the connection using a wire or busbar, and the rest of the items described in 250.28 are out the window. Only a wire or busbar is to make the connection… right? 250.24(A)(4) wouldn’t exist otherwise… right? I have been informed by the inspector that the screws are sized by the manufacturer and adequate, but from what chart?… I need proof! I thought I’d ask here before I ask there. Thanks!