fastline
Senior Member
- Location
- midwest usa
- Occupation
- Engineer
1. An entrance to building being designed. Will have an outdoor disconnect, then to "something", whether that is a pair, or just a single panel board. Thoughts on one better than the other? If we use Aluminum conductors, would like to use 2 sets for the service. How can the tandem set be terminated in the disconnect and panel board?
2. Our area requires that any "conductor" rated over 100A (odd way to say in our code), must be Copper so intent is the stay above that to stick with Al. For that reason, a sort of "busway" type setup is being discussed, in which a larger branch will take off from the main, then pull various terminations to protected disconnects for pieces of equipment. For clarity, consider a 125A branch feeding 3 machines, each their their own disconnect off that branch. It's not ideal, and if any combination of equipment exceeds the need, they all go down, but the bean counting department has determined it will be cheaper to run one branch rather than several. Any thoughts to advice to this? I am wondering about how we will "daisy chain" to these disconnects with only one lug. I don't really like the insulated lug thing unless I have to. Seems there should be a better way.
Also, no way budget will allow for a real busway here. Any branch distance would not exceed about 75ft. I think the general idea was to pepper the walls with disconnects that could be fused to serve different loads as time went on, with little disruption to the system, and keep it cleaner.
2. Our area requires that any "conductor" rated over 100A (odd way to say in our code), must be Copper so intent is the stay above that to stick with Al. For that reason, a sort of "busway" type setup is being discussed, in which a larger branch will take off from the main, then pull various terminations to protected disconnects for pieces of equipment. For clarity, consider a 125A branch feeding 3 machines, each their their own disconnect off that branch. It's not ideal, and if any combination of equipment exceeds the need, they all go down, but the bean counting department has determined it will be cheaper to run one branch rather than several. Any thoughts to advice to this? I am wondering about how we will "daisy chain" to these disconnects with only one lug. I don't really like the insulated lug thing unless I have to. Seems there should be a better way.
Also, no way budget will allow for a real busway here. Any branch distance would not exceed about 75ft. I think the general idea was to pepper the walls with disconnects that could be fused to serve different loads as time went on, with little disruption to the system, and keep it cleaner.