Will disagree here. The definition is:However the NEC does define the term 'Branch Circuit' clearly, and clearly defines an MWBC as a branch circuit (not only in the name but in the definition). And a branch circuit is the entire circuit from the OCPD to the loads, and it is one branch circuit, not multiple ones, because of how its beginning and end(s) are stipulated. So for any branch circuit that is partly an MWBC, the whole branch circuit is an MWBC.
2023 NEC said:Branch Circuit, Multiwire. (Multiwire Branch Circuit) A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a neutral conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral conductor of the system. (CMP—2)
If you want to say that because the start of the definition is "a branch circuit" the definition looks at the branch circuit in its entirety, rather that at any given point in the run of conductors, then the example at hand (a circuit that starts out with a neutral pigtail in the panel that connects to two separate neutrals) does not consist of "a neutral conductor" plus ungrounded conductors. It has two neutral conductors. So under your logic, none of the branch circuit would be an MWBC.
However, the more usual interpretation is that the notion of MWBC is not unitary for the whole circuit, and that part of a brach circuit may be an MWBC, while another part may not be. Certainly that is the only way for which it makes sense to apply a rule like 300.13(B). And 210.4(A) speaks to this as well ("A multiwire circuit shall be permitted to be considered as multiple circuits.")
Cheers, Wayne
Last edited: