Working on a service where there is a 1000 amp service disconnect. Then running a feeder to a wireway feeding individual meters mains. Using the ten foot tap rule.
The utility meters are bonded neutral meter mains. Using the exception for grounded conductor on load side of the service disconnect 250.142.(B) (2). I meet all three, adjacent, no GFP, properly sized grounded conductor.
Using all metal raceways. No wire type EGC from service disconnect to the meter mains.
The question is, would grounding lock nuts be required since these are feeders.
I would think it's a good idea however don't see where it's required unless I missed it some where.