Is an EE-rated fork truck suitable for a Class I, Division 2 area permitted to be used in a Division 1 area that has a gas detection system? The gas detection system would meet the requirements in article 500.7(K)(2). The division 1 area that the fork truck is used in is classified as division 1 due to inadequate ventilation. As far as I can tell, this is allowed per NEC.
However, NFPA 505 doesn't have an exception. Does this mean it overrides NEC?