Good Afternoon, Everyone.
Looking for advice, and I'm feeling very frustrated at this point. Many thanks
I recently had an inspection result on 4/8/2025 in a very old building located in Bronx, NY. I have an objection regarding article 240.24. My overcurrent protection was higher than 6 feet 7 inches, but I have a working platform, which I took for the inspector to work during the inspection. I always bring my NEC book to every inspection, and after that happened, I asked him politely... Would you please measure from the top of the working platform?
things when South
after the NYC Inspector asked for the article section but refused to read the entire NEC code/section.
I got this response from the assistant chief of the Bronx, NY.
"I told you over the phone that you should reach out to the QA unit regarding this. I told you that if you are replacing the entire panel interior "the guts" that it I felt it is within an inspector's discretion to enforce 240.24. But I said that to avoid any confusion to read out QA and also you can request for code interpretation or special permission"
Looking for advice, and I'm feeling very frustrated at this point. Many thanks
I recently had an inspection result on 4/8/2025 in a very old building located in Bronx, NY. I have an objection regarding article 240.24. My overcurrent protection was higher than 6 feet 7 inches, but I have a working platform, which I took for the inspector to work during the inspection. I always bring my NEC book to every inspection, and after that happened, I asked him politely... Would you please measure from the top of the working platform?
things when South
I got this response from the assistant chief of the Bronx, NY.
"I told you over the phone that you should reach out to the QA unit regarding this. I told you that if you are replacing the entire panel interior "the guts" that it I felt it is within an inspector's discretion to enforce 240.24. But I said that to avoid any confusion to read out QA and also you can request for code interpretation or special permission"