solar man
- california
- self emplyed
A one-family dwelling is supplied with a 120/240-volt, single-phase electrical system from the local utility company and has a demand load of 200 amperes. What is the MINIMUM size THWN/THHN aluminum service-entrance conductors required?
In this question - I understand the following -
200 times .83 % - = 166 Amps
What I don't understand is which column to use between 75 deg and 90 deg.
What is the significance of THWN/THHN? Does this mean use either or?
If so - then I would get 3/0 AWG aluminum with a rating of 175 amps ( 90 deg column)
But not sure why the answer is 4/0 AWG with a rating of 180 amps (75 deg column)