MTW
 - SE Michigan
I think you are misunderstanding what it is saying.Tangentially related to this subject... In article 440 (Air-Conditioning and Refrigerating Equipment), article 440.10 requires the SCCR to exceed the available fault current on motor controllers or industrial control panels of multimotor and combination-load equipment. My question is...what motors does this generally include and exclude? My niche is office / K-12 / government / healthcare...not so much industrial/manufacturing/etc.
* chillers, condensing units, cooling towers - obviously yes
* pumps related to such equipment - ??
* packaged air handlers / RTUs that include integral cooling - obviously yes
* packaged air handlers that push heated/cooled air, but do not include integral cooling - ??
* exhaust fans - assume no
* commercial kitchen freezer and coolers
* what else?
(I am aware of the similar requirements in 620.51 for elevator control panels. And of course switchboards, switchgear and panels. Mainly interested in what motors need to be remembered.)
Thank you!
Hi kwired, I understand what it is asking there. My question is "what is air conditioning and refrigeration equipment" as I can't find those terms defined in the NEC.I think you are misunderstanding what it is saying.
All it means is the equipment SCCR needs to be higher than the available fault current, which is the general rule for pretty much all applications when it comes to SCCR.
One reason they maybe put this wording in art 440 is basically a reminder to verify. Many times manufacturers of this equipment do not actually test or at least do not mark them with a rating and the default rating in such cases is 5 kA. Usually not a problem as branch circuit wiring often limits available current at the unit. But really short circuit length could get you over 5kA available at the equipment in some cases.
It is not about the motors. It is about the motor controllers.The question that freezes us is "which motors do and don't need SCCR coordinated".
See art 440.1. Not necessarily a definition there but it does tell us what art 440 does apply to. Key words in there is "hermetic refrigerant motor-compressors" If it doesn't have one of those it is likely either a 422 motor driven appliance or if not that plain art 430 motor applicationMy question is "what is air conditioning and refrigeration equipment" as I can't find those terms defined in the NEC.
Motors don't really need a SCCR. They don't have to carry short circuit currents and be expected to still function after doing so as when they end up carrying a high level fault current they typically are done for and need replaced or rebuilt. A breaker, bus bar, motor controller, etc. however needs to be able to withstand the possible fault current it could carry during a fault event at something it is simply passing current for, and is expected to operate again after the fault condition is cleared.OK...in NEC 2023 I found 430.83 (F) A motor controller shall not be installed where the available fault current exceeds the motor controller’s short-circuit current rating.
So all motors [technically motor controllers, but I'm going to be loose with my language and say "motors"], all motors everywhere, always, should have their available fault current calculated and compared against the controller's SCCR?
I mean, realistically a 1/6 HP exhaust fan is probably under 5kAIC every time (though I haven't really played around with our studies to test that out).
But in absence of established "we know with certainty this equipment will be fine except in the most extreme circumstances", we should be paying attention to available fault current and SCCR - is that right?
This is different from my lived experience of expecting the inspector has eyes on the chiller and elevator SCCRs, and rarely but ~sometimes~ we get asked to verify appropriate ratings on RTUs...and that's it. Are inspectors just assuming the smaller motors are good so they are only looking at the largest ones? For instance I'm surprised we haven't been hit on pumps yet - they can be large, and they are usually located near the service, so I doubt an SCCR of 5kAIC is sufficient.
Do a short circuit analysis comparison using various available currents and 20' and 50' lengths of #14, #12, and #10 conductors. You will find you can rarely see more than 5kA until you start to have tremendously large fault currents on your 15A and 20A circuits. 30A circuits probably need to be a lot more than 50' to get below 10kA. Larger conductor sizes aren't as good at reducing fault currents.mean, realistically a 1/6 HP exhaust fan is probably under 5kAIC every time (though I haven't really played around with our studies to test that out).
Yes you will.We for sure will have CUHs fed with a short run from a panel the main electrical room - we will almost certainly run into some that are over 5kAIC.
Article 110.10 has been in the NEC for some 50 years. Equipment vendors should not be surprised when told the need to supply higher SCCR.I'm going to get some exasperated calls from our mechanical equip reps, ha ha.
I've considered that solution to deal with an 800A chiller - but needed a lifeline much longer than 30' so abandoned it. It is nice to know that we can put that in our back pocket for sticky situations with smaller motors. I assume one should provide signage/labeling of some sort to advise future contractors on the purpose of the coil?It is not unheard of to require a circuit have 20 to 30' of conductor coiled someplace in order to lower the fault current.
Very unlikely...using Bussmann's free app, FC², starting with 100 kA, I get less the 5kA and the end of a 30' run of 12 AWG.Jim & kwired - sounds like I need to run some test studies to see which loads can be considered safe and which loads deserve scrutiny. I agree with the "generally speaking smaller loads are fine" but in our area the utility has some very large short circuit values at commonly-sized 208V pad mounts (52-77kA at 300-500kVA xfmrs), so 120V 20A/1P motors fed out of those main electrical room could be an issue.
Do they make fractional transfer and exhaust fans with larger SCCRs? Cabinet unit heaters with their 1/30 HP fans? We for sure will have CUHs fed with a short run from a panel the main electrical room - we will almost certainly run into some that are over 5kAIC. I'm going to get some exasperated calls from our mechanical equip reps, ha ha.
My understanding is motor controllers are not on the list of equipment that requires the available fault current to be marked or documented. (Such as the requirement in 440.10(B) for AC/refrigeration equipment, or 408.6 for switchboards and panelboards). Meaning a study (or at least an appropriate level of "design thought") is tacitly required for all motor controllers by 430.83 (F) - but absent a requirement for the available fault current to be explicitly marked/documented it is unlikely that inspectors are looking at it there.
NFPA 70E considers testing part of 'normal' activities
I did not say an incident energy analysis and resultant PPE was not required.I think this depends on the type of test being conducted. If you are doing voltage testing on exposed live parts, it's not considered normal operation, and an arc flash hazard evaluation and maybe PPE is needed. NFPA 70E does allow testing to be done without an Energized Work Permittant - one of three exceptions to the requirement.
DonVery unlikely...using Bussmann's free app, FC², starting with 100 kA, I get less the 5kA and the end of a 30' run of 12 AWG.
Also, as far as I know motors do not have an SCCR. The motor controllers and other control devices that carry the actual load current do.
Proper overcurrent protection should interrupt the circuit before conductor is damaged. Conductors can handle well over their NEC ampacity for short time periods, but those short time periods are still much longer compared to the milliseconds that it likely takes for overcurrent devices to operate in such conditions. Look at how small NEC allows an EGC to be compared to what size the circuit conductors need to be as a general rule. If you see an EGC melted down it usually isn't because of fault current but maybe because of a welder not placing his work ground lead close to the work.Don
I am no expert on conductor damage curves, but the idea of serving anything in smaller wire sizes exposed to 100k seems like a poor design choice.
Would it not be better to serve smaller panels first to get the AFC down considerably before serving any of the smaller loads ?
The impedance of the conductor acts as a current limiting resistor, so even with 100kA available at the source, the maximum current with a bolted fault at the end of a 30' run of 12AWG will be less than 2.5kA (yes, I put the wrong number in my previous post). The one cycle withstand current for 12 AWG is 2.7kA. So this one is a bit close. You would have to find the time trip table for your breaker as the actual time trip curves do not give you that detail.Don
I wasn’t picky nits on your numbers…understood your point.The impedance of the conductor acts as a current limiting resistor, so even with 100kA available at the source, the maximum current with a bolted fault at the end of a 30' run of 12AWG will be less than 2.5kA (yes, I put the wrong number in my previous post). The one cycle withstand current for 12 AWG is 2.7kA. So this one is a bit close. You would have to find the time trip table for your breaker as the actual time trip curves do not give you that detail.
However, you will have to find some way to limit the fault current on the line side of the 20 amp breaker that feeds these loads. Unlikely you will find one suitable for use with that high AIC.
Yes. Even fused switches are tested with conductors so a 20A 100kAIC current limiting fuse would also protect #12 conductors.I wasn’t picky nits on your numbers…understood your point.
I looked over prior threads and MOD - JD , I believe, was making the point that if the OCPD was UL 489 then the clearing would inherently protect the wire per the damage curves.