Grouch
Senior Member
- Location
- New York, NY
I understand that motor FLA is used to size overload protection at the starter.
Motor FLC is used to size the conductors and the circuit breaker / fuses feeding the motors.
I also understand that FLC (found in the tables in Article 430) is usually greater than FLA, and is done so to be conservative and to try to capture all different types of motors at a specific horsepower and voltage.
What if you come across a motor whose FLA is GREATER than the FLC values from the Article 430 tables? Do you then use FLA to size the conductors and circuit breakers / fuses feeding the motor?
Motor FLC is used to size the conductors and the circuit breaker / fuses feeding the motors.
I also understand that FLC (found in the tables in Article 430) is usually greater than FLA, and is done so to be conservative and to try to capture all different types of motors at a specific horsepower and voltage.
What if you come across a motor whose FLA is GREATER than the FLC values from the Article 430 tables? Do you then use FLA to size the conductors and circuit breakers / fuses feeding the motor?