A 120/208, three phase system feeds a detached building with a load of 24,960VA using 1 AWG copper conductors. What is the maximum distance the feeder can be to not have a voltage drop of more than 5%?
I calculate the amps first
24,960 /(208*1.73) =69.364
Then I calculate the 5% of the VD
208 * 5% =10.4
Then apply the VD formula for L
L = VD * cmil / 1.73*K* I
L = 10.4 * 83690 / 1.73(12.9)(69.364)
L= 870376/ 1548
L= 562
My answer is 562 ft
But the book says 325ft