Why? The code allows us to fabricate our own NEMA 1 metal wireways and gutters. They are required to be listed just permanently identified with the manufacturer. As such I can modify the can by cutting a hole in it, protecting the edges with suitable round edged edge protection strips and firmly securing the two cans together with bolts or rivets no more than 12" apart, in my opinion. Per article 376.You need something more than just two aligned holes in the two enclosures. If the enclosures are tight against each other, you would use a chase nipple.
Even though the title says "trough", I am reading the language in post #1 that says to me that the right wall of one enclosure is physically tight against the left wall of the second enclosure and that there are aligning holes in the two enclosure walls, but no protection for the conductors running through those holes.Why? The code allows us to fabricate our own NEMA 1 metal wireways and gutters. They are required to be listed just permanently identified with the manufacturer. As such I can modify the can by cutting a hole in it, protecting the edges with suitable round edged edge protection strips and firmly securing the two cans together with bolts or rivets no more than 12" apart, in my opinion. Per article 376.
Yeah the title is somewhat confusing when you read the contents of the OP. I think that you may be correct in your assumption.Even though the title says "trough", I am reading the language in post #1 that says to me that the right wall of one enclosure is physically tight against the left wall of the second enclosure and that there are aligning holes in the two enclosure walls, but no protection for the conductors running through those holes.
I am not aware of any code supporting that. In some areas it common to just cut out a big hole and put some edge guard around it. I can't find a code violation for that.You need something more than just two aligned holes in the two enclosures. If the enclosures are tight against each other, you would use a chase nipple.
Would the two enclosures still require some mechanical connection to each other like being bolted together?I am not aware of any code supporting that. In some areas it common to just cut out a big hole and put some edge guard around it. I can't find a code violation for that.
I don't think so. Is there a code section that you think would? By the way I'm not saying I do it this way, always seemed a little hack to me.Would the two enclosures still require some mechanical connection to each other like being bolted together?
There is flanges for connecting to other enclosures that have smooth rounded edges for your cutout into the other enclosure as well. Connection to the wireway is basically same thing as end caps, couplings, elbows., etc.Most metal wireways I have used can either take end caps or you can order a coupling if you wanted to attach another section. They make 90's as well to go around a corner. I have wrapped them around electric rooms before.
Yes, code requires bolting or riveting in spacing 12" or less.Would the two enclosures still require some mechanical connection to each other like being bolted together?
I agree that is the basics of what the OP is asking, and "as long as you protect the edges and secure them together properly would be the answer."Even though the title says "trough", I am reading the language in post #1 that says to me that the right wall of one enclosure is physically tight against the left wall of the second enclosure and that there are aligning holes in the two enclosure walls, but no protection for the conductors running through those holes.
Does the applicable code mention anything like "mechanical continuity"? I believe the sections for many other "raceways" does use this sort of wording.and secure them together properly
Code reference?Yes, code requires bolting or riveting in spacing 12" or less.
376.100 (B)Code reference?