No adjustment because in the vicinity of the termination, the conductors aren't in a common cable or raceway.Why no adjustment or correction?
No correction because the equipment manufacturer has taken care of that, the specified temperature column of Table 310.16 is your conversion from amps to wire size for that termination.
Of course, through the run of the conduit you have to do adjustment and correction. That's completely separate; nothing we've said about termination is applicable to those checks.
Cheers, Wayne