I don't understand.You just need to trim 1/4 off of one EGC!![]()
I agree. Why this was added to the NEC is beyond me. Was there ever a real world problem with the old method? I'm guessing that the substantiation for a code change for a section that had been around for 50 years was bogus.Doesn't make much sense, seems like it should be 1 count of #10 and 3/4 count of #12.
I don't understand.
The whole thing has never made sense to me. The volume of the conductor does not change based on the function of the conductor. Why aren't all EGCs counted individually like grounded and ungrounded conductors?That's what 2023 NEC 314.16(B) says.
Cheers, Wayne
It actually reduced the volume required when you have an isolated ground receptacle in the box. With the old rule, you had one volume for the normal EGC and a second volume for the isolated ground receptacle grounding conductor.I agree. Why this was added to the NEC is beyond me. Was there ever a real world problem with the old method? I'm guessing that the substantiation for a code change for a section that had been around for 50 years was bogus.
I have only made a few inspections, as I only fill in when our inspector is not available, but cited that more than once. These were so full, I doubt you could have install a receptacle.IMO the entire box fill thing should just be deleted. For one thing, in 25 years, I don't recall an inspector even once looking at and calculating my box full. Second it just seems like a design issue. Any reasonable electrician isn't going to want to fight with a overstuffed box where you have to fight to get the device in and/or take half an hour being as neat as possible to save space . The rule might have some value to a brother in law, but the NEC should be a how to book for DIY's.
Ok, but it still seems like a design issue to me.I have only made a few inspections, as I only fill in when our inspector is not available, but cited that more than once. These were so full, I doubt you could have install a receptacle.
Safety issue when over time the conductors insulation is displaced because they were forced into place when the device screws are tightened and a short circuit or ground fault results.Ok, but it still seems like a design issue to me.
I've been saying that forever. They added barriers to the fill calculation a few cycles ago. I mean really who dreams up this nonsense. A 1/32" sliver of metal and you have to count it but a USB receptacle is the same deduction as a single pole switch. Wouldn't it be better if the devices had their volume marked on them?3rd, it's such an inexact rule anyway with no consideration for what type of size of device.
It is never a good practice to cite a general rule. Much better to cite a real rule.Just imagine all the other things that are wrong or done horribly, it's a lost cause. it's an issue with training and competence. An inspector could always cite 110.2
That is a great idea. There were proposals to require a double volume for the larger devices, but they did not pass.I've been saying that forever. They added barriers to the fill calculation a few cycles ago. I mean really who dreams up this nonsense. A 1/32" sliver of metal and you have to count it but a USB receptacle is the same deduction as a single pole switch. Wouldn't it be better if the devices had their volume marked on them?