srtelando
Member
- Location
- Cincinnati
- Occupation
- Electrical Engineer
Hello,
I'm working on a medium voltage project right now where we are installing a neutral ground resister to limit fault current.
The NGR sits right outside the transformer, but in a separate enclosure.
I noticed that the Impedance Bonding Jumper is defined as the conductor which connects the equipment grounding conductors at the first point of disconnect to the NGR grounded location and must not be spliced.
We are running two parallel sets of 500KCMIL current carrying conductors from the transformer secondary to the switchgear breaker (first point of disconnect.) This means that each set of 500KCMIL conductors will have their own Equipment Grounding Conductor, which normally I would connect to Transformer Frame and Grounding Electrode Conductor. The grounding electrode conductor in this case is connected at the NGR.
My question: Can I bond both equipment grounding conductors from the parallel feeds at the transformer; then run one impedance bonding jumper to the NGR grounded connection? Do I need to run both Equipment Grounding Conductors to the transformer with the current carrying conductors and the run straight to the NGR grounded connection? (In this scenario I would run an additional equipment grounding conductor to the NGR from the transformer frame.)
Any insight on this? Attached is what I think makes the most sense, however, I feel like the violates the rule that the impedance bonding jumper must originate at the first point of disconnect and land at the grounded side of the grounding impedance device without spliced.
(trying to figure out how to attach a picture of my drawing, sorry if you can't see it)
I'm working on a medium voltage project right now where we are installing a neutral ground resister to limit fault current.
The NGR sits right outside the transformer, but in a separate enclosure.
I noticed that the Impedance Bonding Jumper is defined as the conductor which connects the equipment grounding conductors at the first point of disconnect to the NGR grounded location and must not be spliced.
We are running two parallel sets of 500KCMIL current carrying conductors from the transformer secondary to the switchgear breaker (first point of disconnect.) This means that each set of 500KCMIL conductors will have their own Equipment Grounding Conductor, which normally I would connect to Transformer Frame and Grounding Electrode Conductor. The grounding electrode conductor in this case is connected at the NGR.
My question: Can I bond both equipment grounding conductors from the parallel feeds at the transformer; then run one impedance bonding jumper to the NGR grounded connection? Do I need to run both Equipment Grounding Conductors to the transformer with the current carrying conductors and the run straight to the NGR grounded connection? (In this scenario I would run an additional equipment grounding conductor to the NGR from the transformer frame.)
Any insight on this? Attached is what I think makes the most sense, however, I feel like the violates the rule that the impedance bonding jumper must originate at the first point of disconnect and land at the grounded side of the grounding impedance device without spliced.
(trying to figure out how to attach a picture of my drawing, sorry if you can't see it)