ish1284
- Arlington Heights, IL, USA
I have a transformer test report where the %Z is given along with the load losses broken down into I2R losses and then stray losses, and then it totals them together in a third column as total load losses.
I need to use this information to calculate the X/R ratio of the transformer. Is the correct way to determine the "R" component of X/R to consider the I2R losses only or both the I2R plus the stray losses?
Note that there is a separate column for no-load losses which I know not to include. In the example provided, the I2R losses are 159.68kW, stray losses 15.93kW, and total load losses as 175.6kW.