electro7
Senior Member
- Location
- Northern CA, US
- Occupation
- Electrician, Solar and Electrical Contractor
I'm working on a job where we have 3-150kw 3-phase generators in parallel going to a 2000A ATS. The plans from the EE show a 4 pole switch at the ATS. We are interrupting the bus at the gear on the load side of the main breaker. I don't think I want to switch the neutral, but I wanted to confirm. Do I run the neutral through the switch? The plans don't specifically show.
Also, the plans show a ground rod at each generator. From what I remember from a Mike Holt video, there shouldn't be ground rods at generators I thought. Is that correct?
Thanks ahead of time for your input and help.
Sent from my SM-S918U using Tapatalk
Also, the plans show a ground rod at each generator. From what I remember from a Mike Holt video, there shouldn't be ground rods at generators I thought. Is that correct?
Thanks ahead of time for your input and help.
Sent from my SM-S918U using Tapatalk