Grouch
- New York, NY
When running a load calculation to calculate a service or feeder size, I use the nameplate values whether I'm following the standard or optional calculations of Article 220.
For example, I'll use the nameplate wattage of a hot water heater, listed at 240 volts.
If I have, which I always do, a 208 volt service, where in the code does it state that I can downsize the branch breaker for the water heater due to connecting to a 208 volt supply? At 208 volts, the wattage of the water heater (rated at 240 volts) will be derated to 75%. And the current will be derated to about 86%.